Hello,
I have Vitodens 200 with external bivalent hot water tank. Primary source of energy is PVE. I want to maintain temperature of water heated by gas as low as possible (40 °C). I recognised, that hysteresis (temperature when the boiler starts heating of water) is 4 °C below that (36 °C) which is quite cold for shower. I would like to decrease this to about 2 deg but i only found upper limit in boiler parameters. Is there any way to solve it?
Thank you
Hello,
What vitodens 200 du you have?
A new one with the new control technology?
Or an older one with vitotronic controller
the parameter for the vitotronic is in coding level 2 . Code 59.
the default value is 0 with a difference of 2,5K below the setpoint.
for the new controller check parameter "1085.0 „Speicherbeheizung: Einschaltpunkt Sollwert“"
the uper hysteresis can not be changed.
BR