The electric heating for hot water preparation is needed if your heat pump can not reach the set value alone. In the 1x hot water function is heated to the value Temp 2. With TOP is switched off when the set temperature value is reached at the top of the boiler. "Standard" switches off when the temperature reaches the complete hot water tank. The return temperature sensor of the heat pump is used for this. Which attitude is best for you depends on your personal comfort wishes. The activation of the hot water preparation takes place with each setting after the storage temperature sensor in the top of the hot water tank. For this, the current temperature must have fallen below the setpoint by the set hysteresis. On delivery this is set to 7K. Best regards ° fl