Hi all,
I´m a Viessman customer. One year ago I bougth a Vitosol kit and all works fine until this week: the kollector themperature is very high (120-130 celsius degree) but the water is cold (22-24 celsius degree).
My plumber says me that there is air into circuit, and in order to resolve the problem, recharged the circuit,
but after few day the issue occures again.
I think there is a problem with the air relase valve. It´s placed near the Vitocell 200 and not near Vitosolic pannel,
it's rigth ? It's this the problem ? How can I remove the air into the circuit , without have to call my plumber all times and recharge again the circuit ?
Thanks in advance for the support.
Stefano.
Hi Stefano,
normally not air, but a steam bubbles are the problem in solar thermal systems.
The reason for the steam bubbles could be a oversized collector, to less hot water consumption, failure in the solar circulation pump or the pump controller.
In your case the Boiler water is cold, I would suggest a problem with the pump or controller.
After your plumber recharged the solar fluid, did you check the flow-rate on the Taco setter? was there a flow? Does your system have a taco setter, Viessmann systems normally have one.
If there is no release valve at the collector you need this special pump to flush the whole system.
BR